Zambia load shedding 8 hours a day: sizing genset and storage?

A

Ahmed Ben Salah

Verified member · Service engineer

Plant load 320 kW, load shedding for eight daytime hours, grid normal at night.

We have a 400 kVA set but frequent starts and stops and high fuel use.

We want storage for peak shaving. How should battery and genset work together?

Discussion (3)

  • Paulo M.Verified member · Project chief engineer2026-10-31

    Let the battery take the 30-40% fluctuation and run the set at 70% load; lowest fuel and fewer starts.

  • Chanda M.Verified member · Service engineer2026-11-01

    Frequent starts damage starter and batteries; with storage, starts drop from about 20 to 4 a day.

  • Fatou D.Verified member · Procurement lead2026-11-02

    For eight hours of shedding, about 600 kWh of storage suits; log the load first.