Tanzania mine burns 900 L of diesel a day: solar-hybrid payback?
Ahmed Ben Salah
Verified member · Service engineer
Two 200 kW gensets alternate, burning 900 L a day with diesel delivered at USD 1.35 a litre.
Load is 180 kW by day and 90 kW at night; flat land, good sun, no grid.
We want PV plus storage but are unsure of the ratio, and would like real payback figures.
Discussion (3)
Paulo M.Verified member · Project chief engineer2026-09-19
On that curve, 300 kW of PV with 400 kWh of storage is common: it covers about 70% of the day load and keeps one genset at minimum.
Grace W.Verified member · Project chief engineer2026-09-20
Payback must include battery fade: 80% capacity in year five is normal, so show the replacement as a separate line.
Rui C.Verified member · Export inspection2026-09-21
We ran a similar project: four to five years, assuming diesel stays above USD 1.20. A price drop forces a rethink.