Mine fuel farm fire protection: which standard applies?
Kwame A.
Verified member · Mine equipment manager
Two 20 m³ diesel tanks at the mine; the safety inspection says fire equipment is insufficient.
Now there are four 9 kg dry powder extinguishers and a bund.
What standard applies, foam or powder?
Discussion (3)
Grace W.Verified member · Project chief engineer2026-10-01
Diesel is a class C liquid; foam or powder both have a basis, so confirm the local authority's position first.
Chanda M.Verified member · Service engineer2026-10-02
The bund must hold 100% of the largest tank; this is the most common finding.
Ade O.Verified member · Procurement lead2026-10-03
Extinguisher count follows travel distance, not tank count; wrong placement counts as none.