Mine fuel farm fire protection: which standard applies?

K

Kwame A.

Verified member · Mine equipment manager

Two 20 m³ diesel tanks at the mine; the safety inspection says fire equipment is insufficient.

Now there are four 9 kg dry powder extinguishers and a bund.

What standard applies, foam or powder?

Discussion (3)

  • Grace W.Verified member · Project chief engineer2026-10-01

    Diesel is a class C liquid; foam or powder both have a basis, so confirm the local authority's position first.

  • Chanda M.Verified member · Service engineer2026-10-02

    The bund must hold 100% of the largest tank; this is the most common finding.

  • Ade O.Verified member · Procurement lead2026-10-03

    Extinguisher count follows travel distance, not tank count; wrong placement counts as none.